Has anybody had to deal with the grounding of Victaulic piping?

We are currently having discussion within our office on whether or not each section of Victaulic pipe has to be grounding to ensure that the whole pipe line is continuous. Some people are saying that the pipe coupling will isolate each section of pipe therefore requiring a ground strap across each coupling. Other are saying if the pipe support brackets are grounded that that's enough.

Any thought, experiences?

Thanks
 

RE: Grounding of Victaulic Piping

A Victaulic fitting it is a development in which a groove is cut around each end of pipe instead of the usual threads; two ends of pipe are then lined up and a rubber ring is fitted around the joint; two semicircular bands, forming a sleeve, are placed around the ring and are drawn together with two bolts, which have a ridge on both edges to fit into the groove of the pipe; as the bolts are tightened, the rubber ring is compressed, making a watertight joint, while the ridges fitting in the grooves make it strong mechanically. It seems to me this fitting is not destined to be electrical connector. If the pipe is a grounding mean, I don't think this fitting will do the job. If the pipe is not covered with insulating material as pvc or bitumin you need a jumper [see ERITECH Zinc Water Pipe Clamp Erico for instance. ] See: http://www.erico.com/public/library/fep/LT0359.pdf    page 10
If it is insulating covering a based on threading fitting will be necessary.

 

RE: Grounding of Victaulic Piping

2
Victaulic couplings and fittings will provide the necessary continuity for the purpose of grounding and bonding of a pipeline.  The coupling keys are in direct contact with the groove in both the flexible and rigid coupling styles and will maintain continuity actoss the pipe joint.  The gasket simply sits on the pipe OD and is used to span the gap between the pipe ends, it does not offer any electrical insulating properties.  Victaulic couplings in both painted and galvanized meet the UL requirements for Grounding and Bonding Equipment and are listed as such on the UL website.

For additional questions feel free to contact Victaulic Engineering Services at 610-559-3502
 

   

RE: Grounding of Victaulic Piping

Thank you VicEngService!

RE: Grounding of Victaulic Piping

I think that is the definitive answer!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources