I have a Basler DGC-2020 that I've been wrestling with for a few days.

The model I have has 4 output relays. OUT 1,2,3,4.
I have rearranged the logic so ALARM BELL has no output and I've moved it to the GENERATOR BREAKER CLOSE OUTPUT.  However nothing I do seems to ever get the relay to operate.  I've even used the GLOBAL ALARM relay on the GENERATOR BREAKER OPEN signal.  It never changes state either.

I'm led to believe that INPUT_9 and _10 are generated in the Basler's GENBRK assignment code, that is it's nothing I supply physically. That's what the Basler tech told me but then I had the poor chap up at 3AM his time so maybe that is an incorrect assumption..



What's up with this?

Keith Cress
kcress - http://www.flaminsystems.com

RE: DGC 2020

Hi Keith;
I hope that I am not wasting your time.
I see on page 170 of the down loadable manual that IN1 - IN16 are physical inputs. You may need an external jumper. But then there are over 200 pages that I haven't looked at yet, and I'm running out of time this morning.
Good luck.  

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: DGC 2020

(OP)
Thanks Bill.

You're findings are correct. The inputs to the GEN Block are actually external over rides. Stick a logic one in to, say, the close and the output will close immediately.

I think the issue is with the Main Bus Stable conditions I've set.

Keith Cress
kcress - http://www.flaminsystems.com

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources