Multiple feeders from one building to another
I am working on a renovation of an existing school campus. The PE gym is currently fed from a breaker in a panel "MDP1" inside the adjacent (not connected) elementary school building. The school would like to add air conditioning to the gym (a packaged A/C unit setting on a pad outside the building). The existing gym panel "PE", located inside the gym, is too small for the additional load. The elem building panel "MDP1" is also too small to provide the feed, but there is a second panel "MDP2" adjacent to panel "MDP1" that does have sufficient capacity. Can I add a feeder from the elementary panel "MDP2" to feed the A/C disconnect (mounted on the wall outside the gym)?
RE: Multiple feeders from one building to another
Bill
"Why not the best?"
Jimmy Carter
Thanks for the comment. It will be up to the AHJ as you say; he may see the installation as separate from the building electrical with your idea.
The electrical engineer is referencing 225.30 allowing "only one feeder".
Alan
"It's always fun to do the impossible." - Walt Disney
Thanks for the response.
This is a packaged system with everything outside the building (only thermostat and some ductwork inside).
The existing buidling circuits are 120V1PH and 208V1PH fed from a 208V3PH panel located inside the building. The new packaged unit circuit is 208V3PH.
Thanks again,
Alan
Thanks for the comment. I plan to upgrade the feeder so that the installation complies with 225.30.