I have a non load bearing precast prestressed insulated wall panel. I have no drawings but it appears to have 3/8" tendons in each face 16" o/c. Panel are 8ft wide and 23 ft high with supports at base and at 21 ft above slab.
My client wants to install some ~48" wide windows in the center of the panels - thus cutting 2 or 3 tendons.
has anyone had any experience along these lines? Suggestions?
My client wants to install some ~48" wide windows in the center of the panels - thus cutting 2 or 3 tendons.
has anyone had any experience along these lines? Suggestions?





RE: precast prestress concrete wall panels
You will also be taking more vertical load on the two strips due to the window as well.
With the remaining portion of these strips taking extra load, you need to do a design check of one of these strips, with the remaining in-place reinforcing, to see if it still has enough capacity to resist all the loads.
If not, then you either don't cut the window or you add vertical members on either side of the window (we usually use steel tubes or wide flanges bolted to the inside face of the wall, to take all the lateral loads. Then check the strips to see if they can take just the extra vertical loads.