UPS fault
UPS fault
(OP)
Can anyone has any idea as to What Timeout means in reference to Chloride UPS.
We have an alarm for Charger-Timeout & Battery-Timeout, though the Inverter is normal i.e there is no alarm.
We have an alarm for Charger-Timeout & Battery-Timeout, though the Inverter is normal i.e there is no alarm.






RE: UPS fault
RE: UPS fault
Rafiq Bulsara
http://www.srengineersct.com
RE: UPS fault
RE: UPS fault
RE: UPS fault
Also, you need to be careful with these units as a fault can only be cleared by going through the screen menu and actually clearing the fault out of the micro.
Shutting down the unit and restarting doesn't clear a fault even if one has been repaired.
RE: UPS fault
I will try and contact a few colleagues at Chloride to ask what this timeout alarm is if you haven't found out already.
I do know that some other Chloride systems have service alarms similar to a car. If they recommend that your UPS is serviced every year then an alarm will tell you that this time period is up. Once again you will need the software to clear this alarm.
UPS engineer http://www.powerups.co.uk