Accuracy of kWhr metering

Accuracy of kWhr metering

Accuracy of kWhr metering

(OP)
We are involved in a project whereby the consultant are specifying the accuuracy of electrical meters used for monitoring onlyas +/-1%. My expereince is that monitoring is typically +/-5% accuracy and actual metering would be +/-1%. This is a building going for 5 star level NABERS (Australian Green Building) and has monitoring points throughout the building but specific areas for metering.
Has something changed in the building market forcing accuracy (and high cost) up for reasons that seem to be innappropriate?
 

RE: Accuracy of kWhr metering

Oz,

We're seeing it all over the US too.  Of course, the meters themselves are no problem, it's the CTs in that accuracy class that add up to lots of extra money...

Nothing new -- except perhaps that the younger generation of specifying engineers isn't willing to accept anything as inaccurate as ±5%.  I'm even seeing specs for 6-digit displays for real-time air flow rates.  C'mon, we can't even measure that stuff with two-digit accuracy in buildings!!

Good on ya,

Goober Dave

RE: Accuracy of kWhr metering

It's possible there there is legitimate need.  Perhaps the monitoring points could become metering points in the future.

More likely however is that no one has given it much thought, or that the consultant was responding to a last-minute owner request and simply cut-and-pasted from a past spec.



 

RE: Accuracy of kWhr metering

(OP)
Mint
I think it is the latter.
We see more and more specs that have tighter tolerances, because some folk think this will be 'better'. Sure it will, as long as they wish to pay for it.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources