Heat Exchanger pressure drop/flow
Dear all can any one tell me the what will be the effect on delta P and flow if nos of plate incraeses in a plate type heat exchanger keeping same flow at inlet of the heat exchanger
is there any formula to calculate the exact pressure drop/flow
thx in advance
RE: Heat Exchanger pressure drop/flow
Keeping the same flow at the inlet means that the number of plates will not impact on the flow.
I've seen an equation for ΔP in the 8th edition of Perry's ChE Handbook, apparently quoted from APV's handbook.
Santoshdada:
If you can obtain access to a copy, see:
Fundamentals Of Heat Exchanger Design - Ramesh K. Shah & Dusan P. Sekulic, c 2003
Chapter 6, Pages 396-399, Equation 6.44, Example 6.3
SNORGY.
I think the equation to which 25362 refers is Equation 11-79.
SNORGY.