I have double angles acting as vertical X bracing in my structure. Do you consider the whole length of each double angle as the unbraced length? I have asked two coworkers one says you can segment since they are bolted together where the angles cross and the other says we must consider the entire length of the double angle unbraced. Both have valid arguments & I personally design for full length of member unbraced. What are others perspectives on the issue?





RE: V-brace Segmenting
Note that if you're using double angles, you may have to stitch them together to make them act as a unit...
If you "heard" it on the internet, it's guilty until proven innocent. - DCS
http://www.eng-tips.com/supportus.cfm
RE: V-brace Segmenting
RE: V-brace Segmenting
That would not be a bad study to do: See if all the angles or double angles are able to withstand 1% of their axial compressive strength as a point load at their midpoint for all unbraced lengths.
Assume 20' Long angle braces
Uses 2L5x5x7/8 (10' braced length) resists 437k in weak axis.
1% of this is 4.37k
This load at midspan of a 20' span produces 21.85 k*ft @ midspan
2L5x5x7/8 @ 20' length and braced at midspan can take 43.83 k*ft (accounting for Cb using a point load at midspan.
So this appears to work. One thing that isn't accounted for is that the bracing angle is also in tension at this time which may or may not degrade it's capacity. I would think that tension makes the angle more stiff but it also adds tensile stress which can add to the tensile flexure stress. Tension is not codified yet in Chapter H of AISC.
RE: V-brace Segmenting