Balancing valve in heat exchanger arrangement

Balancing valve in heat exchanger arrangement

Balancing valve in heat exchanger arrangement

(OP)
Hi,

Following my previous posts, i would like to ask for another question:

In the image that i attached, there is a balancing valve, that is commonly used. I don't know well why this is used.
For what i undestand, this is used to obtain in this circuit the same pressure drop as the heating device circuit. But, my question is: isn't the 3-way control valve already making that control and compensation?....

thanks
 

RE: Balancing valve in heat exchanger arrangement

This is discussed extensively in thread403-239619: Balancing Valves I ran systems with and without(inherited) balancing valves but I alwasy prefer them.

RE: Balancing valve in heat exchanger arrangement

(OP)
Hi,

Sorry, but i didn't attached the image. Here it goes.

Quark,
For what i've seen in that post that you mentioned, the problem is discussed only in relation to 2-way valves.

Whats your opinion in cases like this with 3-way valves?

Thanks

RE: Balancing valve in heat exchanger arrangement

One function of the balancing valve is that it  makes the bypass have the same resistance as the heat transfer coil set.

OR, If the two streams are very different temparatures and the setpoint is near the temp of one of the streams, then an unbalanced loop would be running near one of its extremes of travel.  the balancing valve biases the loop so that the control valve operates more toward mid-stroke, in its "sweet spot"

Applies to 2-way valves as well as 3-way valves.   

RE: Balancing valve in heat exchanger arrangement

(OP)
Dear JimCasey,

I understand, but using those same arguments, shouldn't we use also a balancing valve at the HX exit? Because if the flowrate thats passes in the heat exchanger also oscilates, the equipment has different pressure drops, and this should be corrected also, or am i wrong in this thought??....

I didn't understand quite well your 2 santence. Can you please explain it again? Thanks

THANKS

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources