Composite metal deck~point load
I have a 4" composite metal deck floor. Steel deck is obviously ribbed and thickness is 0.036 inch. For 4 feet span factored load is 637 PSF. The wheel of scissor lift exerts 110 psi for 4" x 1.5" area. Now
110 psi = 16000 psf per 4 feet = 4000 psf. So deck is not ok. Now contractor will scream If I Ask him to reshore.Am I doing any thing wrong in calcs
RE: Composite metal deck~point load
You should refer to the "Composite Deck Design Handbook" by SDI. It has examples of how to calculate deck capacity for concentrated loads, I think that it even has an example of wheel loads.
h
The number you came up with is more relevant to concrete bearing, not the capacity of the deck. Check out this paper that gives some guidance of how to distribute a point load on a slab.
http://www.njb-united.com/usd/ddds/data33.pdf
I was so glad to see that you posted this paper. Can you please give me any reference, fro where this paper originated, author etc.
many thanks...