A core balance ground ct connection was used in O/L in a Motor,
while residual ground CT connection was used for O/C at the secondary side of Transfomer going to the switchgear where the motor connected.

My question is, can I coordinate the two relays?

What is more sensitive during ground fault?

Thank you.

RE: PDC

Core balance is not subject to CT mismatch, and the CT doesn't need to be sized for load.  Other than that, both measure 3I0 and coordination should be no problem.

RE: PDC

I agree with davidbeach.

One additional comment:
Your core-balance CT's are likely much more sensitive than your residually connected phase CT's.  You may want to check the amount of ground fault current available to ensure that the residually connected phase CT's respond properly.

For example, 2000/5 Ct's connected residually may not allow your relaying to detect a 10A ground fault on a HRG system, but a 50/5 core balance CT would perform very well.

RE: PDC

You also need to be careful in choosing the ratio of the core balance CT to avoid saturation issues if the system is solidly grounded. I looked into a coordination issue recently similar to your situation but the root issue was  the saturation of the core balance CT.

RE: PDC

Hi.
No problem with coordination.
You can put with core-balance CT a low setting..it will about 1% of In of CT ( of course all depend on ) , but with residual connection not less 10-12% of CT rating. Core balance isn't sensetive to CT mismatch, to partial saturation..for example in case of motor start.
That menat, coordination by current setting and by time setting. Standart configuration.
Good Luck.
Slava
 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources