Tilt-up External Free-standing Firewall Connection
3

Tilt-up External Free-standing Firewall Connection

Tilt-up External Free-standing Firewall Connection

(OP)
I'm looking at using precast concrete panels, approx 8m high x 3 m wide, cantilevered from the base.

Are there any recommended clever methods of achieving a fixed base?  At this stage I would consider both; footings cast before and cast after the erection of the panels.

Thanks.

RE: Tilt-up External Free-standing Firewall Connection

Cast the footing with a big slot to receive the panels, set the panels, then grout around the panels.

You can also set the panels on a regular footing and tie the panels to floor slabs.  Need to make a positive attachment to the floor slab.  This method restrains the slab, meaning more likelihood of undesirable shrinkage cracking.

Having said this, if these are external bearing walls, cantilevered walls should not be used.  Walls should be designed to fall inwards when the steel collapses.  A wall which is cantilevered will curl in an intense fire, making it lean out.  The steel will be tensioned, and the connections can fail instantaneously, causing the wall to fail and fall out.

RE: Tilt-up External Free-standing Firewall Connection

(OP)
Thanks hokie

They are freestanding firewalls between transformers in a sub-station, so no issues re connection to steel framing.

RE: Tilt-up External Free-standing Firewall Connection

Hokies method with the cast-in slot is my preferred method, I always ensure this is a tappered slot, makes construction a bit easier.  

When in doubt, just take the next small step.
 

RE: Tilt-up External Free-standing Firewall Connection

In the past I have used ferrules in the slab on either side and the footing at the base to take the push/pull from the overturning. This has worked well and is cheaper than casting a slot in the footing.

RE: Tilt-up External Free-standing Firewall Connection

hokie,

what do you mean when you say a positive attachment?

RE: Tilt-up External Free-standing Firewall Connection

apsix,

I mean providing a tie between the wall and the slab.  Something like spats showed, but it can be done with ferrules and screwed in bars or in other ways.  Don't just depend on the slab each side to restrain the wall, as the slab will shrink away from the wall.

RE: Tilt-up External Free-standing Firewall Connection

spats, if its connected to the slab at the top, why do you need to embed it into the footing?

Those number4 dowels would be a pain, better to have a cast in threaded insert (ferrule) that wont get in the way during lifting.

I do love the footing detail though (when its necessary) I have used similar myself.

 

RE: Tilt-up External Free-standing Firewall Connection

The detail I sent was specifically for a outdoor smoker's lounge, where there happened to also be a slab. It's a small area, approximately 20' x 25'.

I would never consider using the slab for the stability of the wall anyways. What about when it's under construction? You can't remove the braces until the slab is in. What if they decide to cut out the slab in the future, not knowing it's integral to the stability of the wall? Besides, you would have to bury the footing deeper to get a decent moment arm between the slab and the footing. All-in-all, not a good idea, in my opinion.

cds72 - I assume your talking about the slab dowels. Not a problem at all. I've been using them for 20 years and haven't gotten any complaints. They're easily tied to the reinforcing mat, and are not in the way at all during lifting.

RE: Tilt-up External Free-standing Firewall Connection

They would certainly be in the way if you are stack casting.

RE: Tilt-up External Free-standing Firewall Connection

spats,

I agree with the issue regarding the cutting of the slab - it does happen. But if there is a roof at the top restraining it then it will be stable under normal conditions.

 

RE: Tilt-up External Free-standing Firewall Connection

In my experience, stack casting is not used all that much. However, my drawings always contain an "alternate stack casting detail", which uses a deformed bar field welded to an embed plate. I know some kind of ferrule insert is preferred by some engineers, but they're not cheap, nor is having to thread the slab dowels.

cds72: since we were talking about cantilevered walls, there is no roof to brace at the top.

RE: Tilt-up External Free-standing Firewall Connection

Interesting.  In Australia, most of the tilt up jobs use stack casting and ferrules.  And I'm sure they don't do anything they think is expensive.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources