I need to Know about the  Factory Acceptance tests (FAT) for a 13.8KV/0.48 KV  oil filled transformer.
The routine test include
1) Winding resistance
2) voltage ratio & check of voltage vector
3) measurement of impedance voltage & load losses
4) No load los & current
5) Dielectric tests
 seperate source voltage withstand & induced overvoltage withstand test
6) Test for auxillary equipment & wiring
 7) Test on OLTC

   Which additional special test from below are also required
1) Temperature rise test
2) Dielectric test-Lightining impulse test
3) Dielectrica test-PD & Chopped wave LI
4) Measurement of zero sequence impedance on three phase transformer
5) Short circuit test
6)Measurement of acoustic sound level
7) measurement of harmonics on no load current
8) Leakage test for transformer tank.

the transformer is 900 KVA.

Thanks in advance


 

RE: transformer Factory acceptance tests

Is this a standard design or a one-off customm build? If it is a standard design then certain tests might reasonably be waived as 'type tests'.
  

----------------------------------
  
If we learn from our mistakes I'm getting a great education!
 

RE: transformer Factory acceptance tests

zaza123,

From your spec (13.8-0.48 kV)it seems that your transformer is made for ANSI/IEEE stds.

Therefore, if you refer Table 19 of IEEE C57.12.00, it gives a complete list of routine tests and special tests any manufacturer has to carryout as FATs.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources