Transformer zero sequence impedance compared to positive

Transformer zero sequence impedance compared to positive

Transformer zero sequence impedance compared to positive

(OP)
Is it possible that zero sequence impedance is equal to or greater than positive sequence impedance for a power transformer, whose connection is Dyn 11 33/11 kV, 15 MVA ?

RE: Transformer zero sequence impedance compared to positive

Generally not, there isn't generally anything that can add to the impedance in the zero-sequence.  In a bank of three transformers Z0 will equal Z1, as it will in a shell form three-phase transformer.  But, in a 3-phase core form transformer Z0 will usually be in the range of 85% of Z1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources