Service Load Combinations - Section 1605.3.1
Question concerning the ASD load combinations in Section 16-5.3.1 of IBC 2006. Exception 2 indicates "flat roof snow loads of 30 psf or less need not be combined with seismic loads. Where flat roof snow loads exceed 30 psf, 20% shall be combined with seismic loads.
Load combination 16-13 (or LC 6 of ASCE 7-05) is the only load combination that combines seismic effects and snow loads: D + 0.75L + 0.75S + 0.525E. Is this exception saying that for flat roof scenarios where pf is the snow load used in the load combination (in lieu of ps), that the snow load can be disregarded, and for flat roofs with greater than 30 psf snow load, the 0.75 load factor can be reduced to 0.20?
It is a little odd considering that the only LRFD load combination including both snow & seismic also uses a 0.2 load factor for snow. Anyone have any guidance?
RE: Service Load Combinations - Section 1605.3.1
0.20 x 0.75 = 0.15
Am I hearing this correctly?
Mike McCann
MMC Engineering
A definite disconnect between IBC and ASCE7 in this regard.