Help with 15KV Switchgear
Hello all, I have a question regarding 15KV metal-clad switchgear. The facility I am at this week is using ABB 15KV switchgear and supplying it with a nominal voltage of 16,600 volts. I cannot find anything in IEEE that addresses justification for using this voltage on 15KV gear. Any help would be appreciated!
Chad
Chad
Chad Snyder
Director of Operations
American Power Technology
http://www.ampowertech.com
RE: Help with 15KV Switchgear
Jim
How do you KNOW the voltage is that high? Can you see that voltage indication at multiple locations? If this is feeding a downstream device, does that device have its own voltage indication? Does that voltage corroborate this reading?
If you're reading a digital meter, make sure that it is programmed correctly. If it's analog, make sure the meter is scaled correctly. Measure the secondary voltage on the potential transformer circuit and compare it with the KNOWN PT ratio.
Absent all that, a direct reading of voltage with a high voltage tester is called for.
The voltage you're reading is above the manufacturer maximum for the equipment. Liability and reliability issues abound.
old field guy
I'd check the equipment nameplates, and verify the actual operating voltage as already suggested.
"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)
I am familiar with the k factor idea with the old breakers, but was not aware that it could apply to switchgear insulation as well. In an attempt to be lazy and not consult the standards, is this also applicable to the switchgear?
Alan
Alan
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
If the name plate indicates that your swgr is 15 kV rated,then it is based on the standard voltage levels given in ANSI C84.1.Per C84.1,the extreme Utilization voltage should be 14.52 kV,so that the swgr still gives satisfactory performance.
Per swgr standard C37.20.2 the rated maximum voltage should be 15 kV. Also if there are CBs attached to the swgr then their rated maximum voltage should also to be 15 kV (with or without K factor)per ANSIC37.06.
Since you cannot "MEASURE" the "NOMINAL" system voltage,on what grounds would you say that your nominal system voltage is 16,600?So you need to investigate how much is your nominal system voltage at your installation.
Stevenal/racobb,
K factor is relevant to CBs only(old constant MVA concept).Eventhough,the K>1,the rated maximum voltage for the CB should be 15 kV. But depending on the K value,the CB can operate down to a lower voltage (maximum rated voltage/K) with a higher SC interrupting rating (rated SC current x K).
Alan