(OP)
We have four 13.8kV, 8000HP motors which were shipped to pump vendors two years back. They have been lying idle since then. These were manufactured as per API 541.
The time has come to ship these motors to site.

Now the query :
What are the tests to be performed to gauge the healthiness of the motor?

In my opinion, this is equivalent to preventive maintenance tests, only with the exception that these motors were never in service.

Please give your suggestions.

RE: Tests on MV motor

I would follow NETA-ATS (acceptance tests) as a guide plus the motor manufacturer's recommendations!

Rafiq Bulsara
http://www.srengineersct.com

RE: Tests on MV motor

Minimum:  Megger/PI testing and winding resistance test.

Rotate and check for roughness.  Check T.I.R. of shaft extention.

Drain and inspect oil prior to moving the motor if you have oil bearins.  Flush

Think about:  DC step voltage test by competent personnel (it is potentially destructive test but imo with proper test voltage the motor is unfit if fails DC step voltage test).

Really nice:  Run it on a test platform prior to installing.  That is a lot of work and money.  But there are things that can occur during storage such as bow or bearing brinneling that probably may not show up without it.  It is a tradeoff risk vs cost.  How painful is it to find a problem during uncoupled run after installation... sometimes that is no worse than finding it in the shop... sometimes it is completely unacceptable.
 

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Tests on MV motor

I hope these motors were periodically rotated. If they sat idle in one state, it may have sustained mechanical damage e. g. to bearings or shaft may have sagged. (mechanical folks can chime in)

So do not forget mechanical tests. That is why manufacturer's recommendations is paramount.

Rafiq Bulsara
http://www.srengineersct.com

RE: Tests on MV motor

(OP)
The motor manufacturer's guide suggests : Insulation Resistance, PI, DC High voltage tests.
For mechanical tests, they suggest manual rotation ( 10 rotations), if possible, and checking of bearings.

Thanks for the suggestions.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources