Differential Deflection in RCB
We're adding fill to an existing rcb at the end (existing fill tapered to 0 at the end, and we're putting 14' on it to match the rest of the existing). The geotechs are telling us that the settlement will be 3" on that section. The lead structural engineer on the project is worried about cracking in the box due to the differential. However, any amount of differential settlement in the box cranks in huge forces. So even if you can calculate the deflection accurately, the box doesn't "work" structurally in the longitudinal direction by a long shot.
I feel like this is a created problem, since I'm sure that there are plenty of existing box culverts that have had fill added in a future project. Furthermore, it would seem that some differential deflection would have occurred during construction, since the fill varied in the initial condition. Does anyone have experience with this? Is it a problem, or is it something that can be explained using engineering judgment?
Thank you.
Thank you.
RE: Differential Deflection in RCB
When you build something new besides something old whatever the loads, compatibility of deformations obliges the same settlement at foundation, point of contact. In a culvert you have the walls, deep beams along, and if longitudinal settlement becomes a problem you may add flexural strength by diverse ways by adding effectively collaborating steel for flexural stress; and if postensioned (even on brackets!) you may even control and correct the actual deflection to some wanted movement.
I'm trying to avoid modeling - the model I used showed that the box was overloaded even with minimal deflections (3/4"). I have very generic and useless foundation springs from the geotech, so modeling really doesn't get me a reasonable answer, unless the answer is to rip out the box and rebuild it, which I'm convinced is unnecessary.
So, have you (or anyone else) had experience adding load to an existing box? Were there deflection problems?
The differential settlement can be used to calculate the forces that will result in the box, only they must be based upon some assumption of box stiffness.
Now, normally, you would initially use the overall gross moment of inertia of the box (assuming it is uncracked). But this means you have a very stiff box being deflected 3" and will produce the highest bending stresses in the section.
But most likely, with the uncracked, gross moment of inertia, you will exceed the cracking stress in the concrete and thus the stiffness of the box will immediately reduce. If the box is reinforced properly, the hope is that the cracks would be somewhat distributed along the length of the box but that might not be the case - you could get one large crack relieving all the stress at one spot.
So if it cracks, is there a problem? Might be that soil would slowly erode into the crack and cause sink-holes above. Some type of hydraulic grout plug might be attempted. Could be expensive.
If the cracks are well distributed and the rebar holds the concrete together, you may not have a problem.
I used cracked section properties in my model, but even with that reduction in stiffness, the loads were well beyond capacity.
The lack of longitudinal bars (#4 @ 18) makes me think that this isn't an issue for boxes. I doubt that any box would settle exactly the same in every location. It's notable that standard boxes are constucted with expansion joints every 30'...it's possible that maybe it's a small enough distance that all deflections are taken by the joints and each piece sees limited load.