Parallel transformers in ETAP
Hi I am trying to connect two transformers in parallel using the electrical modeling program ETAP but I keep getting an error:
A loop condition has been detected for Panel2 and its downstream elements.
I assume this means there's a ciculating current ?!?
RE: Parallel transformers in ETAP
Both transformers belong to the same vector group?, in other words the phase shift is the same through each?
Both transformers have the std positive seq, -30 degree secondary phase shift
How are controlled the tap changer positions?
I have not modified the tap positions of the transformers.  I have left them as there default values of 0 % tap on both the primary and secondary
Is it not possible to supply two tranformers in parrallel from a panel using two different breakers?
My set up works fine when I supply the parallel transformers directly from the utility but when I supply them through the panel I get the error saying a loop condition has been detected
Maybe you need to have separate secondary busses for the transformers, then have very low impedance connections from those busses to the common secondary bus.
"Maybe you need to have separate secondary busses for the transformers, then have very low impedance connections from those busses to the common secondary bus. "
I tried this out but still seems to give the looped condition
My suggestion is contact ETAP technical support. They should be able to help you resolve the issue. I have been using ETAP for several years. Its tech support engs. are very good resolving my questions.