Angle Braket Loading Calculations
Hello Guys:
I am in need of assistance. My task is to build a support made out of Steel Angle Brackets as a means for supporting a duct system. So far I have not advance to a point that I can proudly proceed with my task. Can anyone help me determine the allowable loading for a given Steel Angle Bracket. Lets say that I would like to utilize a L 5" x 3 1/2" x 3/8" bracket to support a vertical load laying evenly on top of it. The steel angle bracket is to be supported at both ends by means of other two sets of angle brackets (vertical positioned) which are to be attached to I-Beams. I have available to me the eight edition of a manual of steel construction book. Can anyone be so kind and provide me guidance on how to utilize the values given in such manual. I also do not clearly understand the given data in that books. Please advice.
RE: Angle Braket Loading Calculations
A sketch would be helpful.
The top and bottom angles will act compositely like the top and bottom flanges of a beam, due to the stiff rods between them and the fact that you will not have lateral wracking due to the confinement at the box beams.
Given that, the likely control will be shear at the top and bottom angle ends. The loads are relatively small (350 lb+/-)at each load point, so you have less than 2000 lbs total load on the system. If you treat the system as a beam, the tension in the bottom angle will not likely be critical but check it to be sure...then check the shear in the angles at the ends. The bolts into the box beam will be in shear as well, but shouldn't be an issue if you are using 1/2" or so diameter expansion or epoxy anchor bolts.
First off I would find the second moment of area of your compound beam using the Parallel axis thereom, I estimate this to be 329in^4 for your configuration ignoring any contribution from the vertical rods and assuming the angles take all the bending.
Once you have the second moment of area you can use the standard bending formula to find the stress in the angles ie:-
σ= M*y/(I)
where M= max bending moment
y= distance to extreme fibre from neutral axis
I= second moment of area
This should give you a start.
regards
desertfox
Nonetheless your problem can be solved either with uniformly or with concentrated loads and the differences in bending stresses being the prevailing type, should not be significantly different.
I would also draw a shear and moment diagram to get a better idea where and which max stress should be analyzed.
You should however be more concerned about deflection and that should be your main focus of the analysis. If you determine your Z value based on some allowable deflection, you'll find out that stresses will be well within your allowable working stresses.
DESERTFOX:
It has been a while since I had to perform calculations to find the moment of inertia (second moment) of a compound beam. I dug out my statics and mechanics of materials book and read the section on "Deformation of prismatic member possessing a plane of symmetry and subjected at its end to equal and opposite couples acting in the plane of symmetry." As I read to the derivation, it gave the formula below that you provided:
"σ= M*y/(I)
I= second moment of area"
Can you help me on the calculations to determine the second moment of a given angle support and how to apply the parallel axis theorem? Does the parallel axis theorem is to be utilized to translate the moment of inertia to the neutral axis? How is the angle support ought to be treated to calculate the second moment since a square beam is not geometrically shaped as an angle bracket? Please advise and thank you in advance.
http://
I'll try and help over the next couple of days, at present I am working away.
Try looking in your text books for the parallel axis theorem it should come under either its own heading or compound beams.
desertfox
try this link and go to chapter 15 of this online book
h
desertfox
i figure you need to to both, but your post started with the supports and without seeming to get to an answer you've gone off onto the conduit.
this can be a very simple problem. you've found a static textbook, great. the analysis starts with assumptions. very simplistic and reasonably accurate is to say that the support react their nearby load (a span of load for the intermediate supports, 1/2 span for the ends). Alternatively you can use more complex (and accurate) methodologies like "3 moment equation" ... google it if it's not in your text. this'll tell you the reaction at your supports, which should bring up a host of questions.
next calculate the maximum moment in the conduit beam; if you use the simplistic reactions it'll be PL/4 (where L is a span and P is the load of a span) ... this is conservative (bigger than the more accurate solutions, like "3 moment equation").
So now you can analyze the conduit beam. Important assumption, how are the 10 conduit going to react the moment ? are they going to bend together, as if they are one welded assembly, or are they going to slide against one another ? i think it's conservative if you say one tube reacts 1/10th of the moment.
but that's enough for now ...
if the latter, i think you should start your own thread, and not hijack someone else's.
Have you considered asking a structural engineer? I wouldn't try to design an amplifier from a handbook.
tg
The formula for parallel axis theorem can also be found here
http://www
desertfox
I have uploaded a file showing how I got the second moment of area for your compound beam.
This assumes all the bending would be taken by the angles and is conservative as it takes no acount of the vertical studs.
This is only a small portion of the calculations your faced with, you need to look at bolt loads connecting your beam to its supports etc
desertfox
Thank you for the uploaded file that shows how the second moment for the compound beam was found. I understand the second moment for each of the angle brackets was found and then it is translated to the neutral axis. My question is how did you now where the neutral axes was to be found at 17.0984/2? Please advice
If a beam as symmetry in that plane then the neutral axis occurs at the centre of the shape.
So for instance a rectangle, square and a standard "I" beam will have the neutral axis at the centre of the shape.
Look up neutral axis in your text books.
regards
desertfox
do you really think that those two (ok, four) angles are going to bend together like a beam ? i guess, obviously, you do.
i'd rather see each angle as an independent beam, carrying 1/4 of the load.
nonsinusoidal,
you're asking very basic questions, and i don't think you should rely on this forum to completely answer them all. i think you need to either find a structures guy where you work, or 2nd best, find a structures text to help you. as desertfox has said, "This is only a small portion of the calculations your faced with".
Yes I believe a pair of angles as shown in my uploaded file will act as a composite beam due to the connecting rods.
Whilst I appreciate they might be some small local bending between the vertical rods I think this will be small, I likened it to castellated beams in buildings where they burn out the centre web to reduce weight which is also based on the assumption that all the bending stress is carried by the beam flanges so I am led to believe.
Your method would be very conservative and theres nothing wrong with that.
desertfox
Thank you for all of your responses.
RB1957,
Unfortunately, structural engineers are not a part of my organitation. However, my original question has not been answered (It was diverted). My original question was as follows:
"I have available to me the eight edition of a manual of steel construction book. Can anyone be so kind and provide me guidance on how to utilize the values given in such manual. I also do not clearly understand the given data in that books."
Please advice as appropriate.
my advice, pick one of the following ...
1) find a structures textbook that will explain all the things you need to look into to solve this problem;
2) maybe a building code will explain what they want checked (and i think they also say how to check); or
3) if there are structures people in a different part of your organisation, go find them.
You need to specify which properties your asking about, it is unlikely that we can give you a detailed answer to all the things you would like to understand however we might be able to point you in the right direction.
desertfox
1) Since when is 880 / 2 angles equal to 220?
2) I would use simple support, so wl^2/8, not wl^2/6
Agree that crippling is the failure mode, as long as by that you mean lateral/torsional buckling. I'd use the full length as unsupported. Loads are so low, it may still work.
Desertfox:
The angles are linked by vertical ties, and NO DIAGONALS OR SHEAR WEBS, so there is no composite action. Just take the total load per support assembly and divide by 2 angles. Better yet, I'd assume one angle could take maybe 60-65% of the total, and sleep better.
tg
"σ= M*y/(I).................. and the rest.
OMG!
no
OMFG!!!
The two horizontal angles are indeed supported by two vertical angles. Since my expertise do not fall withing this subject matter, I would like to know if you can explain what you stated below:
"The angles are linked by vertical ties, and NO DIAGONALS OR SHEAR WEBS, so there is no composite action. Just take the total load per support assembly and divide by 2 angles. Better yet, I'd assume one angle could take maybe 60-65% of the total, and sleep better."
Thank you for your assistance in this matter.