protection of Control-transformer
A Motor Control Center has been dimensioned  for 460V ,630A,25kA. A feeder of 25kA-MCCB  supply  a  6.23kVA-7.82A motor –pump,  with a 2-phase derivation for a control-transformer 480/120V-70VA for control circuit of motor-pump.
Control Transformer is protected by   460V-10kA-MCCB .
Question is:- Should  MCCB control transformer dimensioned  for [b]25kA[b] instead of [b]10kA[b]?.
Is there any recommendation?
RE: protection of Control-transformer
This is a control power transformer for one starter?  Put a current-limiting fuse on the primary and eliminate the circuit breaker.
"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)
Thanks Itsmoked. I guess we do not have Class CC rejection Fuse in my country.