Oil burner AHU system design
I'm designing a oil-fired AHU heating system, but I'm new to this kind of system, so any help will be greatly appreciated.
The system will be using diesel fuel oil, and have a ceiling hung AHU with a oil burner section in it.  There's a fuel tank outside of the building.  The building is a single-story building and the location is in Alaska, so the outside design temp is lower than -30F.
I understand that the AHU will require a gravity day-tank.  So, I know that we have an AHU, a storage tank, a day-tank, a pump somewhere.
That's all I know about the project.  Could somebody walk me thru how to complete the system, such as what other equipment is needed, where to locate them, and how to hook them up?
Thanks.
Michael
RE: Oil burner AHU system design
Do you have a sketch?  Storing anything hot in an Alaskan winter will be very in-efficient or very expensive.  Why not direct fired oil burning heater?
I would say call up a vendor for direct fired units in Canada. Those guys deal with that kind of design and worse everyday.
You will have to combine various code & standards and the burner manufacture's requirements to design the fuel delivery system. Start with the fuel oil burner such as http://www.powerflame.com/pdf/HAC-ServiceManual.pdf I would find out the required piping details such as recirculation lines sizing. Next local codes & standards such as IMC & NFPA for fuel oil piping are very helpful to specify piping materials. Next, work with the tank vendor on piping requirements for a heated external storage tank and lift / transfer pump requirement - you have 2 tanks. Finally review with the insurance carrier on the size, quantity and hazard of fuel oil storage tanks.