Electrical/Comm. cable separation?
Electrical/Comm. cable separation?
(OP)
Electrical and comm. cable being serviced in 4" pvc conduit. Shouldn't there be separation between the two cables? Electrical cables coming from 300kVA transformer.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Electrical/Comm. cable separation?
|
RE: Electrical/Comm. cable separation?
In general, there is no NEC requirement for separation below 1000V, as long as all circuit are insulation for the highest voltage in the conduit. So, it is not illegal to put a 24 V dc analog signal cable in the same conduit with a 600 V power circuit, as long as the signal cable has 600 V insulation.
This does not mean that there won't be interference problems.
"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)
RE: Electrical/Comm. cable separation?
Also, if you dig into Article 800, it is also not permitted to mix power-limited with normal power circuits. There are exceptions pertaining to circuits which are soley to provide power supply to communications equipment. Or if there is a permanent barrier.
RE: Electrical/Comm. cable separation?
RE: Electrical/Comm. cable separation?
RE: Electrical/Comm. cable separation?
Any other communications cable type your just making noise for the comunications running them in same conduit. I guess this would be just be bad practice but still lawful within NEC or whatever spec that would allow it.
RE: Electrical/Comm. cable separation?
"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)
RE: Electrical/Comm. cable separation?
Minimum Separation Distance
from Power Source at 480V or less
CONDITION <2kVA 2-5kVA >5kVA
Unshielded power lines or
electrical equipment in proximity
to open or non-metal pathways 5 in. 12 in. 24 in.
(12.7 cm) (30.5 cm) (61 cm)
Unshielded power lines or
electrical equipment in proximity
to grounded metal conduit pathway 2.5 in. 6 in. 12 in.
(6.4 cm) (15.2 cm) (30.5 cm)
Power lines enclosed in a grounded
metal conduit (or equivalent
shielding) in proximity
to grounded metal conduit pathway - 6 in. 12 in.
- (15.2 cm) (30.5 cm)
Transformers & electric motors ------- 40-in (1.02 m) -----
Fluorescent lighting ------- 12-in (30.5 cm) ----
NEC 2001, article 800.52
Communications cables can't be bundled in the same sheath with Class 1 circuits. Class 2 and Class 3 circuit conductors can be in a sheath with communications circuits, if the Class 2 and Class 3 circuits are contained in listed communications cable or multipurpose cable.
Communications conductors can't run in any raceway, compartment, outlet box, junction box, or similar fitting with conductors of electric light, power, or Class 1 circuits, but there are exceptions.
*
Separate the conductors from the power or Class 1 conductors by a barrier.
*
Introduce power circuit conductors only to connect to the communications equipment. The power circuit conductors require at least 0.25 in. of separation from communications circuit conductors.
In other applications, you must separate communications conductors by at least 2 in. from any electric light, power, or Class 1 circuit conductors, unless you install those conductors per a Chapter 3 wiring method, such as raceway, metallic or nonmetallic sheath, or UF cable.
RE: Electrical/Comm. cable separation?