Emergency panel in Hazardous area

Emergency panel in Hazardous area

Emergency panel in Hazardous area

(OP)
anyone can give me the answer.

Regarding Lighting panel was located in hazardous area and TNS system need 3 phase + N ,my question related to all power incomer cable  need to have switch for cut neutral cable or not,
If switch incomer only 3 Pole and no switch at nutral ,Is it dangerous ?

RE: Emergency panel in Hazardous area

Jed057,
Any 3 Ph. electrical feeder that supplies a load situated in a hazardous area shall be equipped with a 4 poles switching device.   
This is to mitigate the hazard that may appear due to accidental existence of potential difference between neutral and earth, which can represent a source of ignition (i.e. a spark capable to ignite the flammable surrounding atmosphere).  



 
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources