Wind loading on a large garage door (horizontal slider).

Given the following parameters:

V = 90 mph                
I = 1.0
Kd = .85
Kz = .98
Kzt = 1.44

ASCE 7-02 Section 6.5.10:

qz = (.00256)*Kz*Kzt*Kd*V^2*I
   = (.00256)(.98)(1.44)(.85)(90^2)(1.0)
   = 24.87 psf

Now for the C & C design wind pressure for a low rise building (< 60') see

ASCE 7-02 Section 6.5.12.4:

p = qh[GCp-GCpi]   where

GCpi  =   .55
GCp   =  0.90
      = -1.00

then p = 24.87*[0.90 -.55] = 8.71 psf

or
        p = 24.87*[-1.0 – (-0.55)] = -11.19 psf

This just doesn't see right to me for the wind load on a large garage door.  The magnitude of the difference between positive and negative pressure seems about right, but I'm thinking the values should be about double what I get; what do you fellow designers think?  Where am I going wrong?
 

RE: More Windy Componets & Cladding

You have the internal pressure coefficients reversed.  When there is external pressure on the door, assume there is internal suction (0.9 + 0.55).  Likewise, with external suction, internal pressure (-1 - 0.55).

DaveAtkins

RE: More Windy Componets & Cladding

(OP)
OK, so switching those around results in:

p = 24.87*[0.90 -(-.55] = 36.06 psf

or

p = 24.87*[-1.0 – (0.55)] = -38.54 psf

I fill better, although that's a pretty hefty wind load. It is about 18 psf more than in Table 1609.6.2.1(2) for Walls in Zone 4.  Any thoughts on that?

Thanks Dave!

RE: More Windy Componets & Cladding

Those are large C&C wind loads but it appears the cause of their magnitude is because you have a topo factor (Kzt = 1.44) that has driven them up a bit.

 

RE: More Windy Componets & Cladding

On large flexible doors, you will end up with catenary forces on the ends, meaning you will have to design the end connections for shear, but also axial forces.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources