Digital I/O Control Cable with Multiple DC Voltages
I have required digital input wiring from a switchgear to a VFD terminal strip rated probably <24Vdc. At the same time, I have digital outputs (dry contacts) coming from the same VFD terminal strip to the switchgear and these contacts will operate on 125Vdc powered from tge switchgear.
My question is that: Can I use one multicore cable for both digital inputs/ouputs although some will be 125Vdc and some will be <24Vdc?
I believe that this will not be an issue if I will use a 600V insulated cores and the fact that both are digital signals and are both <600V.
RE: Digital I/O Control Cable with Multiple DC Voltages
From technical point of view, no problem.
From maintenence point of view, ...I like separate between few type of DC.
125V DC?
Keith Cress