Smart questions
Smart answers
Smart people
Join Eng-Tips Forums
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

jcroley (Electrical) (OP)
23 Jun 09 10:29
I have a 3 wire vs. a 4 wire question for you folks out there.  My primary transformer has a 12470 volt, 3 phase delta primary - 4160Y2402 secondary.  However, my loads on the secondary of the transformer are all 3 phase, 3 wire loads (large motors).  Can I ground the XO terminal on the secondary of the transformer at the transformer and not pull a fourth wire into my switchgear, or is that neutral wire required all the way through the system?
Helpful Member!  REDDOG (Electrical)
23 Jun 09 11:08
You need to bring the neutral in to the service equipment and ground per NEC requirements.This ground can be solid or reaistance.
The neutral is your ground fault return path.
jcroley (Electrical) (OP)
23 Jun 09 11:12
Thanks Reddog.  This was my plan - I was pretty positive that was my only option, but I kept hearing from folks that the neutral could be terminated at the transformer.  Just didn't sound right.

Jim

Thanks,

Jim

antigfk (Electrical)
23 Jun 09 12:42
jcroley,

You kept hearing from folks that the neutral could be terminated at the transformer because it is common practice and done all the time.  You take a ground conductor - terminate it on the X0 bushing and terminate the other end to your ground system... usually a ground rod.  The transformer tank will also have a ground pad which should be connected to your ground grid via a ground cable.

RedDog is right that the connection between X0 bushing and ground can be solid or it can have an impedance (resistor or reactor).

The NEC requires you to run a ground conductor(s) with the phase conductors from the transformer to the switchgear.  Conductor 1 will be run from the X1 transformer bushing to phase A bus at the switchgear.  Conductor 2 will be run from the X2 transformer bushing to phase B bus at the switchgear.  Conductor 3 will be run from the X3 transformer bushing to phase C bus at the switchgear.  The ground conductor must be connected to the transformer ground bus and the other end must be connected to the switchgear internal ground bus.  The switchgear termination box will usually have a ground-bus near the bottom of the enclosure that is bonded to the transformer tank - which should be bonded to the ground grid.
rbulsara (Electrical)
23 Jun 09 13:07
I agree with antigfk. What Reddog said (bringing N to service equipment) is only applicable to systems of less than 1000V.

NEC also requires "additional" ground connection of X0 at the "outdoor" transformers. (with or w/o impedance).

 


 

Rafiq Bulsara
http://www.srengineersct.com

odlanor (Electrical)
28 Jun 09 16:02
We used bringing N to service equipment only to systems less then 1000V AND 4 WIRE.
sberbece (Electrical)
29 Jun 09 22:25
jcroley,
 
If your transformer will always be used to supply 3 wires connected loads, you could save the neutral cable between the transformer and switchgear. However, you may want to consider installing a CT inside transformer's LV junction box, to supply your earth fault protection scheme.  

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Back To Forum

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close