L1 is hot, is L2 common and L3 gnd? Searching the entire net and all I can find L1, L2, L3 is 3phase.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
single phase motor L1, L2, L3
|
RE: single phase motor L1, L2, L3
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: single phase motor L1, L2, L3
RE: single phase motor L1, L2, L3
Keith Cress
kcress - http://www.flaminsystems.com
RE: single phase motor L1, L2, L3
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: single phase motor L1, L2, L3
RE: single phase motor L1, L2, L3
htt
http:
I m aware that L1, L2, L3 is 3 phase, but...and I also have another 110vac mtr that has the hot marked L1 and the common marked L2. Make a rule and ppl brake it.
RE: single phase motor L1, L2, L3
On 1 phase equipment intended for use in the US, they will often mark the leads as "L1 and L2" because of the fact that they may be capable of being used on a 1 phase 120V circuit, OR reconnected to be used on a 1 phase 240V circuit. Yes, in the 120V circuit the designation could show L and N, but L1 and L2 is fine as well. On the 240V circuit however, L and N would be incorrect. So showing L1 and L2 is the universally acceptable alternative.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: single phase motor L1, L2, L3
It's 3 phase.
BK
RE: single phase motor L1, L2, L3
"On the 240V circuit however, L and N would be incorrect."
Blimey! We've been doing it wrong in the UK for a hundred years...
----------------------------------
If we learn from our mistakes I'm getting a great education!
RE: single phase motor L1, L2, L3
paul
RE: single phase motor L1, L2, L3
Or did you interpret that as meaning "us" instead of US, and then took the "Royal us" version to mean people on the island of Great Britain?
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: single phase motor L1, L2, L3
Eric Kench, P.E.
RE: single phase motor L1, L2, L3
Now, in North America, if we connect 240 V transformers in wye we will have a 240/416 V system.
If we now take 120 volts from a center tap on a 240 volt winding, one end of the winding will still be connected to the system neutral. Hence the Neutral/0V-115V-230V configuration in the UK.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: single phase motor L1, L2, L3
RE: single phase motor L1, L2, L3
Yes, but those motors do not have a L3. The "TEFC 3P" tells you it's 3-phase. Typically, there is a seperate square for "Phase" on the nameplate but they didn't bother clarifying that data on this motor.