Best Location for CT Grounding

Best Location for CT Grounding

Best Location for CT Grounding

(OP)
Hi everyone,

I would like to know where is the best location to ground the CT secondary "one point only"

is it at SWGR CT Box, LCC or relay panel?

and why?

thanx

RE: Best Location for CT Grounding

http://www.netaworld.org/files/ItemFileA877.pdf

It depends....

"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)

RE: Best Location for CT Grounding

(OP)
thank you dpc

RE: Best Location for CT Grounding

Hi SMB1
Please see attached thread, it was intresting.
thread238-211553: CT grounding.

BTW, I start change my opinion smile.
Best Regards.
Slava

RE: Best Location for CT Grounding

Your wye or delta connection should be made at your ct termial block.Your ground should be located in the breaker if the relays are in the breaker.  If the relays are in a control house then the ground should be there.  This will reduce the chance of your differential relays operating for an external fault.

RE: Best Location for CT Grounding

I agree with all of the above points in regards to CTs for protection applications.

I'll throw in one thought though for CTs for high-end metering applications.

For EHV metering applications, particularly generation metering, shielded/twisted-pair cabling is used between CTs in the switch-yard and the meter in the control house. The CT secondaries are still connected in a grounded-wye, but the common point is made at the meter and then grounded there. The concept of only 1 grounding point still applies, as multiple grounding points is also a "no-no" for metering circuits due to the concerns of circulating ground current distorting the meter readings.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources