translate motor label

translate motor label

translate motor label

(OP)
I can't read this, can anyone help?
I think it says 460 and 265vac
1.05 and 1.85 amps
60Hz
0.45wk=0.6HP
1660 rpm?
is torque listed and what about phase?
What is that above the Hz and below?

tks much, p

RE: translate motor label

I'd assume "TRIFASE" means three phase.  

Torque is not given.  1.05 Amps at 460 V, 1.85 Amps at 265 V.   1660 rpm.   Power factor = 0.78  0.45 kW power output at the shaft.

Assume the Y above the 60 Hz indicates a wye connected stator and I assume the H is insulation class.

Arrivederci,

Dave

"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)

RE: translate motor label

You have a six lead motor which may be connected in either wye or delta.
The line currents are different, but the current through the windings is the same with either connection and the voltage across each individual winding is the same with either connection. All the line current passes through the windings on the wye connection but the line current splits into two windings on the delta connection. That is the reason for the apparent discrepancy in currents.
C = connection; in the corroded area you may make out a triangle. This is the symbol for wye/delta.
Cl = insulation class H

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: translate motor label

So what you really have is a 50Hz dual voltage Y-Delta motor designed to be used in countries where they have 380/220V motors, but it has been re-rated for 60Hz operation at 460V. The Delta voltage rating of 265V is technically accurate, but impractical because there is no 265V source in use anywhere. It is only on the nameplate as a vestige of it having been originally designed for use in IEC countries. So if you intend on using it in the US, consider only the Y connected (460V) ratings as Bill said above.

But if you are in a 50Hz country, you can still use it as a 380 or 220V motor. The speed will be 20% lower and thus the kW capacity will be 20% lower.

This by the way is a high slip motor, that's why the PF is lower than what is generally considered normal. That means the torque response to a load change may be different than you would expect with an average motor.


"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln  
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies  

RE: translate motor label

(OP)
I hooked it up to 3phase 0-230vac motor control and it did nothing. I opened it up and it looks much worse inside then the outside. Rust and dry inside the gearbox. Thanks for your help. Now on to my next project...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources