Substation NESC 161.A
Substation NESC 161.A
(OP)
We just received a new substation switchgear and the control wiring to the feeder breakers (and generally everywhere) is #14awg. The control circuit is protected by a 30A breaker (per feeder breaker mfgr GE). The switchgear mfgr claims he is only obligated to follow ANSI C37.20.2 which says size the wire for the anticipated steady state load and overcurrent is not a consideration. However, our utility follows NESC and para.161.A says that a conductor and its insulation must be protected from overheating by overcurrent, alarms, indication or tripping devices. A #14awg wire cannot be protected by a 30A breaker. Question 1: Is there a grey area here?
Question 2: If the switchgear manufacturer is OK to do this, are we OK to install new circuitry into the switchgear using his requirements only? (We were going to add a completely new annunciator with #18awg wiring and protect it with a 20A panel breaker claiming the switchgear mfgr's logic. I would like to see us protect it with a 10A breaker instead. Our #18awg 90 degree C wire can handle 14A.)
Question 2: If the switchgear manufacturer is OK to do this, are we OK to install new circuitry into the switchgear using his requirements only? (We were going to add a completely new annunciator with #18awg wiring and protect it with a 20A panel breaker claiming the switchgear mfgr's logic. I would like to see us protect it with a 10A breaker instead. Our #18awg 90 degree C wire can handle 14A.)






RE: Substation NESC 161.A
I would follow NEC ampacity tables for auxiliary power wiring even though you are exempt as a utility. Also, you can't size the breakers for the 90°C insulation rating if the terminals are rated for 75°C (normally the case). The NESC and NEC are installation standards, not equipment standards, and do not cover the manufacturer's internal equipment wiring.
RE: Substation NESC 161.A
The switchgear manufacturer insists that he does not need to consider overcurrent concerns but will size the wire such that it will handle the steady-state anticipated loading of the wire (per ANSI C37.20.2). There is no further fusing downstream of the 30A breaker. He does run #10 awg from the DC panel to the first terminal point in the feeder compartments and then uses wiring is #14 awg.
However, we are going to add stuff in this switchgear and because we are under NESC, we cannot size breakers less than the wire ampacity I don't think.
We now have a switchgear where some of the circuits have a 30A breaker protecting a #14 awg wire by the switchgear vendor and then our 20A breaker that protects a #12 awg wire (per NESC) because we put it in. Does this seem contradictory?
RE: Substation NESC 161.A
Happiness is a way of travel, not a destination.
RE: Substation NESC 161.A
RE: Substation NESC 161.A
RE: Substation NESC 161.A
It is quite common to see larger field wires and smaller wires inside the equipment for the same current. Once you start dealing with installation codes, you must accept that the results are not always logical or the most cost-effective solution. Conductor sizing requirements in the NEC are only partially based on the physics of current-carrying capability of the conductors.
"Theory is when you know all and nothing works. Practice is when all works and nobody knows why. In this case we have put together theory and practice: nothing works... and nobody knows why! (Albert Einstein)