concrete column retrofit
concrete column retrofit
(OP)
A client needs to fix a failing concrete column. The problem is corrosion. It appears that moisture from a very humid indoor environment has started corrosion from the bottom and is working its way up the column. The bottom 18" of reinf. is severely corroded, allowing the column to crush and spawl. I was thinking of removing the damaged material and encasing the lower half with a reinforced concrete jacket. It's 14" diam., about 8' tall, supports a concrete beam and is on a 48" sq. pad foundation. It's in a utility room. Using the pad dimension to assume the column load, the column design seems to be more that adequate. It's not part of the lateral force resisting system. The plans provided aren't enough to determine the applied loads.
'Anyone have advise?
'Anyone have advise?






RE: concrete column retrofit
RE: concrete column retrofit
Mike McCann
MMC Engineering
RE: concrete column retrofit
No, I don't have a photo. The damaged area has vertical cracking, bulging & spawling outside the rebar. The ties are rusted through and broken. The verticle bars,(6)#8's anf (6) #6 ftg. dowels, are really bad. It's like peeling bark off a tree. It's pretty hammered.
I think the extent of the damage is limited to the bottom.
The entire column seems to be protected with Thoroseal or something.
I'm wondering if it makes better sense to cut the entire bottom third off & add an 24" or so pedestal W/ epoxied dowels. There would be a pinned connection I guess. Cleaner, & the rust will be gone.
If this is a common problem, someone should have a better fix.
RE: concrete column retrofit
A concrete jacket might not stop the cause of the corrosion.
RE: concrete column retrofit
Mike McCann
MMC Engineering
RE: concrete column retrofit
I think you are on the right track. Typically if a concrete column is not too severely corroded, the vanilla method is to remove the loose and deteriorated concrete, clean the rebar, add rebar or other reinforcing if necessary, and replace the removed concrete.
In your case, it sounds like the corrosion is excessive so removing and replacing a significant portion of the column might be the way to go.
The other response to this is to verify what caused the moisture/corrosion in the first place (per JedC above). If there is moisture coming in from above, then some remediation of the waterproofing is in order. If it is simply a wet environment, and will continue to be wet, then perhaps other measures could also be included such as sacrificial anodes, epoxy rebar, concrete mix corrosion inhibitors (DCI for example), etc.
RE: concrete column retrofit
RE: concrete column retrofit
It may be worth getting a concrete repair company on board, their reps will often come to site and give you advice. They may be able to tell you straight off what the cause of the problem is.
Once the required chemical considerations are taken care of then it is simply a matter of restoring the load path.
RE: concrete column retrofit
I'll go back and take a closer look. I'll find a concrete repair company.
I'll call the original engineer if possible to confirm the loads.
It's definitely going to take epoxy rebar & some kind of seal at he ground level. I don't think the soil is naturally highly corrosive. Could calcium chloride additive have this kind of effect?
Assuming the footing rebar is corroded, what do you think about just making the pedestal large enough to spread the load instead of R&R of the footing?
RE: concrete column retrofit
1) If bulging is occurring, I would highly recommend some shoring of the beams be placed immediately. You will also need shoring when chipping out the concrete...especially if you have to chip to sound concrete...be careful how much you chip out.
2) You need to identify the source of the probably...if you dig deeper you will always find other areas/elements of concern. Is it moisture and/or concrete chemical properties. I would request a material testing and investigation program be performed in the area of concern as well as another part of the structure. The question: Is this a localized issue or a global issue? Older concrete sometimes have chlorides from admixtures...and if their is a waterproofing issue...then it gets activated. Need to define extent of problem, and stop cause.
3) Would recommend spraying all concrete in the area with a migrating corrosion inhibitor.
4) Jacketing the column with new concrete is probably preferred in this case. I would also add anodes (pucks) inside the mix. Make the mix expansive with low water cement ratio. Make sure to prep surfaces properly.
5) Call Structural Group (Structural preservation Systems) for help.
RE: concrete column retrofit
By preping the surfaces, do you mean acid etch & bonder?
I've alerted the original engineer via e-mail. If this were my project, I'd want to know about it. I'll wait for his response.
Either way, this has been a learning experience. Migrating corrosion inhibitor and anode pucks? I'm impressed.
Thanks
RE: concrete column retrofit
RE: concrete column retrofit
'Turns out there are no plans or calcs. to be found. The project engineer said there was a water intrusion problem about 20 years ago. There are no visible signs like stains on the block walls. I think the room houses pool equipment, pool acid, chlorine, etc. That's probably the cause.
I'll just recommend further investigation, handle the column problem & move on. I'm thinking 24" sq. x 24" to 36" pedestal with epoxied epoxy coated rebar, 4,500 psi type V concrete (maybe with anodes (pucks)). If further retrofit is required elsewhere, this still needs to be done, even if temporary.
agreed?
RE: concrete column retrofit
RE: concrete column retrofit
Thanks
RE: concrete column retrofit
What apparently is the concern is that if you use the epoxy coating for replacement bars, the oxidation of the bars is actually magnified due to concentration of the electrical current (from oxidation) at the point where the epoxy ends and the original non-coated bars begin.
There are conflicting opinions on this and you should check them out. ACI has a very good repair document out there that discusses this...not sure of what it is but do a search on the ACI website.
RE: concrete column retrofit
I think my epoxy coated bars will be some distance from the Rusted bars in the footing. The rusted bars in the column will be gone.
RE: concrete column retrofit
RE: concrete column retrofit
RE: concrete column retrofit
There are proprietary sacrificial anodes that can be embedded into the concrete to avoid the above mentioned corrosion. Once again I would recommend you seek advice from a reputable manufacturer.
RE: concrete column retrofit
RE: concrete column retrofit
On preping I would recommend chipping to sound concrete and then coating the surfaces with either a latex bonding agent or a epoxy based agent. I use SIKA products for these sort of repairs, like Sikatop 123 and Sikadur. You'll need to consult their spec sheets for application. Sika also has epoxy products for coating the reinforcement which has corrosion inhibitors in them. Ferroguard is the pucks.
Use Guide.
http://ww
http
http
yes, be careful with using epoxy coated bars and pucks...you may just shift the corrosion problem to another part of the structure....maybe even right next to the repair. I highly recommend finding out what is causing the corrosion.
RE: concrete column retrofit
RE: concrete column retrofit
Your advise has been helpful.
I think I'll recommend finding an expert in this field for the corrosion investigation and mitigation. I lack the expertise.
RE: concrete column retrofit
The manufacturer such as Sika will give you the options, but it will still be up to a structural engineer such as yourself to do the final specification as it needs to be structurally adequate.
The structural adequacy you understand, the chemical and durability considerations will be addressed by their rep. I see no need for you to offload it to someone else.
Also, manufacturers like Sika usually have a list of approved repairers who know what they are doing, so the site work should not be an issue.
RE: concrete column retrofit
htt