Breaker failure protection
2

Breaker failure protection

Breaker failure protection

(OP)
Hi everybody
good morning
I have a small question. In breaker failure protection, whether we have to use  a separate secondary core of the CT or we can use the same core as used to other protection system eg over current protection ? What is the general practice. Could anybody let me know
regards
Rajendra

RE: Breaker failure protection

2
Hi.
It's depend on your application ( votage level) and rules in your/customer companies.

Up to 35kV in lot of companies use BFP built in in the relays.
For subtransmission and transmission level usually used separated core for BFP it's part from BBP.

In few companies BFP is part of CB control relay and that means, separate core.

For my pinion, preferd separate core.

Hope it help.
Best Regards.
Slava

RE: Breaker failure protection

(OP)
This is intended for 132 kV transmission line of length 6 km .
 

RE: Breaker failure protection

Hi.
If you have some problem with additional core, you can use same core as protection or used built in BFP into protection relay.
It's also OK, don't worry.
Best Regards.
Slava

RE: Breaker failure protection

(OP)
hi
Thanks a lot for your kind response
regards
Rajendra

RE: Breaker failure protection

Most modern relays are capable of doing their own breaker failure protection, no need for separate relays or separate CTs.

RE: Breaker failure protection

Many breaker failure schemes require an input from a protective relay to start the breaker failure timer. So to have an input from a protective relay, it must be seeing current from a good CT. So that good CT can be used.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources