Tray Cable under raised Computer Floor

Tray Cable under raised Computer Floor

Tray Cable under raised Computer Floor

(OP)
It is my contention, with an inspector, that running Tray Cable under a raised Computer Floor, supported by uni-strut, is permitted by the NEC under 336.10 (7).  Do you agree?

RE: Tray Cable under raised Computer Floor

As long as you are in an industrial facility where the conditions of maintenance and supervison ensure that only qualified individuals service the installation and the cable is marked as type TC-ER, this section applies.

If this is a commercial buidling or an institution (school, hospital, etc) this seciton does not apply.  If it is a data center, you have to argue that a data center is an industrial installation.  I'd call it more a commercial building.

Good luck

RE: Tray Cable under raised Computer Floor

(OP)
It is in an industrial facility, but it is type TC cable.  I took the reference to type TC-ER as a specific instance of when the cable left the tray and was unsupported for 6 feet to utilization equipment; then you must use type TC-ER.

RE: Tray Cable under raised Computer Floor

Interestingly, if your data center qualifies under article 645, TC can be routed loose under the floor.

Alan
----
"It's always fun to do the impossible." - Walt Disney

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources