precast prestressed plank modification
I have a n existing precast prestressed plank space that a new user wants to modify, requiring greatly increased overall loads as well as new significant partition loads. Any ideas on how to go about strengthening this stuff? Can I create new bearing points to reduce span length/increase capacity? Or d I have o essentially frrame a new floor above the existing?
RE: precast prestressed plank modification
Additional bearing (support) points to increase the capacity would not be recommended as this may cause the plank to fail - literally explode. Not good.
Have you though about the foundation impliations yet?
Mike McCann
MMC Engineering
Jike: If the PT is straight and centered, that would probably work. I would defer to the manufacturer though.
Mike McCann
MMC Engineering
impact on foundations will be analyzed, but as a preminary the additioanl floor load is not large compared to overall total floor loads
The new floor I am considering is a steel platform structure above existing floor. Of course this reduces headroom. And of course I am limited by what can be carried up in a freight elevator.
Most plank that I am familiar with has straight tendons in the bottom. If fire rated, they might have increased cover but generally not centered.
The scheme uses a cable, one or two posts. The cable pushes up the posts against the floor, so you may make it a participant from the start even for the already existing load, something you won't achieve with passive methods. You may also use an active poncelet truss, essentially a number of the named system for 1 post, with active cables, also.
Do not forget to examine the long term relaxation of the cables in its amount, and the deflections under exploitation of the renewed structure, for if not it could lead to a serviceability problem midterm, specially with partitions above.
This way yo may use the existint support or strong points, but will require additional structural floor thickess. If subsumed in the required ceiling and no conflict with equipment, could be a solution.
2. It may be simpler and factible depending upon the case adding bottom steel or carbon fiber reinforcement and top steel (or concrete), made to work conjointly.
I don't see much feasible posttensioning an infilled core without too much trickery within the hollow cores and above the structural floor, weight could be unsurmountable problem.
Assuming the planks are pre-tensioned prestressed, then the prestress is transferred via the bond between the concrete and reinforcement.
The planks are probably designed as simple spans and are designed for sagging moments only.
If you add an intermediate support, you will get a hogging moment that the plank will not have been designed for, and it will snap.
However if you saw cut the plank at the intermediate support it then becomes 2 simple spans, with a reduced span length and thus should be able to support more load. (If the planks are post-tensioned then you could not do this)
Being able to calculate what load the reduced spans will support will be the tricky part, if you have no info regarding the design of the planks.
OR
external post tensioning with a quenn post in the middle of the span? This would greatly increase your strength and stiffness. Could also work around existing utilities.
Call Structural Group (Structural Preservation Systems)
How did you get the rebar/grout assembly in the cores to behave compositely with the plank? Some kind of special non-shrink bonding grout?
That would be right, but if the support is provided and the top is sawn immediately, the condition you described will not occur. You would just have two simple spans. Jike's solution will work, provided the centre support is allowed.