Detection of CT secondary open circuit on a running system
Detection of CT secondary open circuit on a running system
(OP)
Good day
We had a failure of CT in a 6.6KV Motor feeder panel due to one secondary CT wiring connection was loose/Open in the terminal block. Is there any kind of online detection system or relay to detect the open circuit in the CT Secondary circuit. We are using SEPAM 2000 relay for the Protection purpose and I could not find any feature in this relay to detect if any one PHASE current is not available. Since I am doing the study to recommend a solution to avoid CT failures in future, your expert advice is appreciated.
Best regards and Have a great day
We had a failure of CT in a 6.6KV Motor feeder panel due to one secondary CT wiring connection was loose/Open in the terminal block. Is there any kind of online detection system or relay to detect the open circuit in the CT Secondary circuit. We are using SEPAM 2000 relay for the Protection purpose and I could not find any feature in this relay to detect if any one PHASE current is not available. Since I am doing the study to recommend a solution to avoid CT failures in future, your expert advice is appreciated.
Best regards and Have a great day






RE: Detection of CT secondary open circuit on a running system
I don't know this relay.
You can check few optioms ( 99%, Im sure, this relay is included one of the options) All are same, only other naming.
1. CT supervision
2. Curennt supervision
3. Current condition monitoring
4. Broken phase detection
etc.
More or less this functionality is base on the simple principal: (Imax-Imin)/Imax, from time to time ( depend on relay type) used Iavg.
In few type relays it's used as protection in case of loss of primary phase, in few in additional to protection function, used additional function: current supervision function for alarm.
But I never see some special CT open circuit online monitoring. You can't separate. what happened: open CT circut, CT fault or loss of primary phase.
In special application like to 87B ( BBP) used term CT open circuit supervission/detect for avoid maoperation of BBP.
But it's build on the diff current level
Hope it help.
Best Regards.
Slava
RE: Detection of CT secondary open circuit on a running system
Thanks again
Best regards
Ramesh
RE: Detection of CT secondary open circuit on a running system
Regards
Marmite
RE: Detection of CT secondary open circuit on a running system
Regards
Ramesh
RE: Detection of CT secondary open circuit on a running system
If you have a way to compare the vector sum of the three phase currents (i.e the residual current) with a MEASURED neutral current, then you could also alarm if the difference is too great, as this is sometimes caused by loss of input from one of the 3 + 1 CT circuits.
RE: Detection of CT secondary open circuit on a running system
Sramesh, Im fully agree with Marmite and tinfoil.
What Marmire saied, all newer relays are included this option.
Good Luck.
Slava
RE: Detection of CT secondary open circuit on a running system
RE: Detection of CT secondary open circuit on a running system
Thanks David for the valuable suggestion, I will discuss with Schneider Electric on the possibility of modifying the logic of the existing SEPAM 2000 relay,which will avoid buying new relays.
Thanks again and Have a great day
RE: Detection of CT secondary open circuit on a running system
RE: Detection of CT secondary open circuit on a running system
David, you recommned build invert logic of 60 functionality
Best Regards.
Slava