Settings calculation BB protection HV network
(OP)
Please can you inform based on experience settings Id and Istab of BB protection of type relay siprotec Low impedance numerical protection 7SS/
In the substation when there are different ratio of CT from the smalest 200/1A and bigest ratio 2000/1 in bus coupler there will be problem of saturation in these case for external short circuit
In the substation when there are different ratio of CT from the smalest 200/1A and bigest ratio 2000/1 in bus coupler there will be problem of saturation in these case for external short circuit






RE: Settings calculation BB protection HV network
You must read recommendation of mnf.
Possible few option of calculation.
This difference ie not so important 2000:200A 10:1 , nothing for this protection. You can choice setting about 80% of max load current on the station, or used 2000A, as max load current and put setting on the 1600A. Istab is angel in this protection, if I remember right.
Saturation is not problem, 7SS5 have all algorithms, problem is second SC, in the same time, at zone of BB.
Best Regards.
Slava
RE: Settings calculation BB protection HV network
RE: Settings calculation BB protection HV network