Arc Flash calculations in IEEE 1584
Arc Flash calculations in IEEE 1584
(OP)
How is there a min. and a max. fault current?
What causes a min. and a max.?
Thanks
What causes a min. and a max.?
Thanks
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Arc Flash calculations in IEEE 1584
|
RE: Arc Flash calculations in IEEE 1584
There are minimum and maximum bolted fault currents based on the strength of the power system. For example, say your plant is fed from a high voltage line between two utility substations. With both substations feeding your plant, you may have a "maximum" amount of fault current available. With the "stronger" substation de-energized, you are only fed through the "weaker" substation and therefore you have a "minimum" amount of fault current available.