I have been doing some wind/seismic calculations for relatively light structures.  The wind forces are much higher than the seismic forces in this case due to site locations.
When using the equivalent lateral force procedure I come up with basically a percentage of the weight to use as my base shear.  In the high-seismic areas, how high can this percentage get?  Just wondering what would be the all-out worst case?  50%?  I deal with seismic on such an infrequent basis that I don't have a good feel for the numbers.
RE: Seismic percentage
It really varies depending on your seismic response factor R which is determined by your material and type of construction.  From ASCE 7-05 Table 12-14.1 you can have R values ranging from 1.5 for plain concrete to 8 for buckling restrained braced frames.  Normal light framed wood construction is 6.5.
In Washington State which is moderately high seismic the percentage of horizontal load to weight for a wood framed structure usually runs below 16%.  My understanding is when you get into the range of horizontal acceleration greater than about 25% the equations aren't realistic.
Referring to ASCE 7-05-
Pg. 220 shows areas with Ss=300% = 3.0
Then Fa=1.0 maximum, Sms=3.0, SDS=2.0
In Table 12.2-1, R can be as low as 1.0.
I, importance factor, can be 1.5.
Then Cs = SDS/(R/I)= 3
And V = Cs * W = 300% of W in 12.8.
That's not to say you'd actually see this- you'd try to use a structure type with higher R, for example.  And the jobs I've seen where seismic loading was really high also had site-specific response spectra, so you weren't working off of standard code provisions.