In load combinations E = Ev + Eh. All our designs have been Cat. A so per code i've been able to ignore the Ev values. Per the inspector we are required to design as a Category B for this particualr site. Per ASCE 2005 12.4.2.3 the Ev value is accounted for in the factor on DL. My question is Ev really a verticle load and if so How would you distribute this vertical component on each level/column? Or, is this Ev additive to the Eh value?






RE: Vertical Seismic Load Component.
So the Ev portion of the E could be included as a factor on your D load in a computer program load combination....such as 1.34D where it might be 1.2D (gravity) plus 0.14D (for Ev).
Also include it upward as well so you would also have a 1.06D (1.2D minus .14D).
RE: Vertical Seismic Load Component.
It certainly doesn't hurt to run the 1.2D - 0.14D (from Ev) case, but I cannot ever see it controlling.