(OP)
I am doing part sizing and selection for a circuit of mine.  Was curious to how much current if any a motor starter coil will pull.  It controls 480V 3 phase squirrel cage but is 120v controlled

RE: Coils

Can't answer that with the little info you've provided.  The bigger the motor the bigger the starter.  The bigger the starter the more current it draws. And yes, they all draw current.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Coils

(OP)
1/2hp motor.  I am trying to size my transformer.   

RE: Coils

(OP)
WEG TEFC(IP55)

my fault - 3HP motor

full load current 3.9A
Loacked rotor 30.8A
No load - 1.75A

All based on 480V numbers

RE: Coils

Remember to take inrush current into account.
Those little control transformers have a rather bad "voltage regulation".
That means that voltage drops a lot when loaded with unexpectedly high current. The contactor coil usually does just that. So it starts closing the contacts, coil voltage drops and contacxts start opening. Not good.
Make the transformer at least five times nominal coil power. Ten times is even better.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Coils

Go with a 50 or 75VA transformer.  Don't forget your motor needs electrical overload protection.  And your control transformer needs 460V fuse protection.

You can buy packaged "Motor starters".  You should consider it.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Coils

I was going to suggest 50 VA. Pretty common for small starters.  You can usually find the coil current listed in the catalog.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Coils

  The namplate current is used to size the overload protection. You would have to use NEC Table 430.250 to determine the actual full load current. This value according to the information that you have given for a 3 phase 3 HP 480 volt motor is 4.8 Amps.
  Starters have a horsepower rating which would have to correspond with the motor hp. You must find a starter that matches the horse power rating for your motor otherwise use the FLC values as determined from the NEC.

Eric Kench, P.E.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources