In one of the industrial systems, 33kV and 6.6kV voltage levels are being used by using 220/33kV and 33/6.6kV Transformers. In refurbishment project, 11kV supply is required. As there is no spare feeder available in 33kV level, we would like to derive 11kV supply from 6.6kV switchgear by providing 6.6/11kV Transformers. Pl. discuss pros and cons.
Advanced Thanks for your partcipation...
In one of the industrial systems, 33kV and 6.6kV voltage levels are being used by using 220/33kV and 33/6.6kV Transformers. In refurbishment project, 11kV supply is required. As there is no spare feeder available in 33kV level, we would like to derive 11kV supply from 6.6kV switchgear by providing 6.6/11kV Transformers. Pl. discuss pros and cons.
Advanced Thanks for your partcipation...






RE: Step-Up Transformer
RE: Step-Up Transformer
RE: Step-Up Transformer
Please give us a more information.
What is a size of 33/6.6kV trafo?
What is power demand for the 11kV, hou match bays you need at the 11kV swg, how match infeeds to 11kV?
For example, some crazy idea, replace your 33/6.6kV trafo to 3-winding trafo 33/11/6.6kV.
Best Regards.
Slava
RE: Step-Up Transformer
Rating of 220/33kV Transformer:100MVA
Rating of 33/6.6/6.6kV Transformer: 40/20/20MVA
Existing load on 6.6kV wdg: 12MVA
Estimated 11kV Load: 2.5MW@0.85p.f
Other than "unusal", I am looking for any technical constrains of using 6.6/11kV Transformer of this network configuration.
RE: Step-Up Transformer
I don't see any problem from electrical point of view.
Maybe, will extra losses, not more.
But...
You have check with factory technology connection between 11kV and 6.6.KV.
What I meant, loose of 6.6kV is loose of 11kV. What happened with end product. Are it same line of product?
Are it separated process?
Best Regards.
Slava
RE: Step-Up Transformer
RE: Step-Up Transformer
In this case: I don't see any problem.
From time to time I see in industrial such applications.
Used "old" substation or "low" level of voltage as stand-by source. Problem is only losses on stand-by trafo.
Good Luck.
Slava
BTW, to your other Q, one of big generator mnf., siaed, that in-rush of GSU is not a problem for generator.