Hello everybody.

I looked over at NEC and didn't find an answer.

Please point me where to find this information, minimun separation distance between electrical (power, lighting, control) cables and instrumentation (F&G, service, J1, J2, J3, ESD, SIS, Telecom, etc) cables in above ground instalations (trays).

Thanks in advance.

Best Regards.

MARCO

RE: Electrical / Insrumentation trays separation distance

That's because NEC doesn't care if any of your circuits work or not!  They just want to prevent fires and to a much lesser extent electrocution.

Because of the various susceptibilities and noise sources that abound you won't find a Standard.  You may find some corporate or industry guidelines or rules.

Search in here for "cables separation control".

Keith Cress
kcress - http://www.flaminsystems.com

RE: Electrical / Insrumentation trays separation distance

The classifications you list don't mean much in NEC land.  

Anything over 1000V must be separated.  Below that, you're on your own - use company standards or best practices.  

The NEC does require that all cables in a common tray, conduit etc must be insulated up to the highest voltage in use.  So if you run 480 V circuits in the tray, everything else must be insulated to that level.  

But itsmoked is very correct - the NEC is mainly a fire prevention standard, not an installation specification.  

"The more the universe seems comprehensible, the more it also seems pointless." -- Steven Weinberg

RE: Electrical / Insrumentation trays separation distance

I have often seen a metal barrier in a tray, this allows you to run HV and LV cables in the same tray with zero spacing.
Roy

RE: Electrical / Insrumentation trays separation distance

(OP)
Thanks for the replies.

The idea is not to run E&I cables in the same tray with a barrier but to use separate trays for each cable types but using the same support (same threaded rod in a hanging arrangement) and I don't know the separation distance between trays and since NEC doesn't have an answer I guess I'll just have to use 300 or 350mm.

Regards

RE: Electrical / Insrumentation trays separation distance

MARCOPEREZR,
                           300 - 350 sounds OK, the trays need enough spacing so you can get your hands in to lay the cables

Roy

RE: Electrical / Insrumentation trays separation distance

300 mm is what is used in most European paper mills and steel works. So it is probably fine.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Electrical / Insrumentation trays separation distance

(OP)
Yes, 300mm sounds OK, the problem is that the client is requesting a document or specification stating that 300 is enough I can't find such information, I will continue looking.

Regards.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources