minimum footing requirements for shear wall?

minimum footing requirements for shear wall?

minimum footing requirements for shear wall?

(OP)
I did calcs for a long building which required existing hallways to be upgraded to 1-hour fire resistance.

Since these walls were being re-paneled anyway, I used the shear resistance to qualify the resisting capacity of the building.

The walls sit on a 4" slab.

The entire slab is surrounded by a 12" below grade perimeter footing. So, I can qualify the bearing beneath the slab as 1500 PSF, and the walls have only 100 PLF.

Does anyone foresee problems at review? It was submitted today.  

RE: minimum footing requirements for shear wall?

The only problem I can see is with the required 3" clearance from the soil to any reinforcing steel, to include thge anchor bolts.  Normally I thickebn the slab under ther shear wall to 8 to 12" to accommodate this.  

I assume with a long wall that holddowns were not needed and that if seismic governed for the gyp that you used half sgtresses for the shearwall capacity?

Mike McCann
MMC Engineering

RE: minimum footing requirements for shear wall?

what the shear resistance has to do with fire resistance? where is the shear resistance came from, by reinforcing dowels? Sorry, I don't understand your question.

RE: minimum footing requirements for shear wall?

(OP)
msquared,

That is a good mention. I thought of it in process, then forgot it.

Using IBC 2006 Table 1911.2, I can spec .25" dia. bolts @ 4' o.c. (500# shear allow). The embed is only 2.5", leaving 1.5" clear.

Plus there is a vapor barrier.

RE: minimum footing requirements for shear wall?

(OP)
In the end, I changed my shear distribution almost entirely to proposed wall sections. Where I had to distribute to existing walls, I spec'd powder driven nails at 6" o.c.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources