Isolation vs regulation in Power Transformers
I don't understand the differences between types of transformers. Specifically, what are the differences between isolation transformers, regulating transformers, and power transformers.
I was under the impression that ANY transformer, with the exception of autotransformers, were isolating and regulating devices. What part of theory did I miss?
RE: Isolation vs regulation in Power Transformers
Gunnar Englund
www.gke.org
An isolation xmfr is being installed mainly to create isolation, typically for fault limitng but increasingly for harmonic mitigation.
A regulating xmfr (typically with automatic on-load voltage control) is primarily intended to control/regulate the load-side voltage around a set point.
A power transformer usually incidcates a larger device thana distribution xmfr, but this one varies a lot by region.
But, again, if all transformers are, in a sense, isolation devices (agin with the exception of autotransformers), what makes them different? I read something about separate windings and insulation, but unless it's an autotransformer, those are a given for all of them. I also read something about separate bobbins, but other than separating them physically more than they are already, what difference would that make?
But basically, any two-winding transformer is an isolation transformer.
"The more the universe seems comprehensible, the more it also seems pointless." -- Steven Weinberg
Thinking about a current transformer, the voltage and current on the secondary side are completely isolated from the common mode voltage between ground and the high side terminals.
From Std C57.12.80
regulating transformer: A transformer used to vary the voltage, or the phase angle, or both, of an
output circuit (referred to as the "regulated circuit") controlling the output within specified limits, and
compensating for fluctuations of load and input voltage (and phase angle, when involved) within specified
limits.
power transformer: A transformer that transfers electric energy in any part of the circuit between the
generator and the distribution primary circuits. See also: distribution transformer