Uni-strut and clamps used as fire sprinkler pipe hangers

Uni-strut and clamps used as fire sprinkler pipe hangers

Uni-strut and clamps used as fire sprinkler pipe hangers

(OP)
WE are seeing more and more cases of unistrut type systems fastening sprinkler piping to building structure.  If oriented so that piping is not hanging down against the clamp, the shear or slip load limits are small enough so that the piping does not meet the 5X weight of water-filled pipe + 250 pounds from each point of attachment per NFPA 13. Anyone else seen this?  Would appreciate an AHJ point of view also.  

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

I hate seeing this sort of thing.  Not your question but uni-strut clamps on sprinkler systems.

I can't find uni-strut clamps anywhere in the FM Approval Guide or UL Listing for fire sprinklers.  If they are not there you can't use them unless you can get a PE to sign off.

From a personal standpoint I'd go with using a uni-strut clamp to secure a 1" inspector's test drop to a wall, I've never met anyone that would object to that yet, but hanging mains is a different story.


 

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

Unistrut is strictly forbidden here.

RE: Uni-strut and clamps used as fire sprinkler pipe hangers


"Unistrut is strictly forbidden here."

Please explain you lost me here.  Forbidden?

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

Simply put, if a local fire marshal were to see sprinkler pipe hung from unistrut, he would not allow occupancy in the building.  

This is just my local AHJ's stance on unistrut.
 

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

It appears that Unistrut obtained FM approval for fire protection service:

http://www.unistrut.com/DB/PDF1/SWIFT-GRIP_flyer.pdf

I would need to research the listing but on the surface it looks as if this system can specified for hanging fire protection piping.

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

Looking at the pdf - it looks like it is the clamp (looks like a modified beam clamp) not the unistrut structural members that have received the FM approval.

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

(OP)
Thank you for the input.
I should have been clearer on the type of clamp I was referring to...it is one that actually rides in the strut.  The answers confirm what we have maintained, that typical unistrut and pipe clamps are not listed for fire sprinkler piping use.

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

There's a whole chapter devoted to hangers. If the only criteria were listings, this wouldn't be the case. 9.1.1.6.1 and .2 address the trapeze hanger that I believe seehorn would be referring to? If the pipe is laid upon the strut and the clamp is merely used to secure it I don't see a problem. If the clamp is actually used to support the weight of the pipe, then 9.1.1.2 applies and you require an engineer to sign off on it.

Regards
Dave  

RE: Uni-strut and clamps used as fire sprinkler pipe hangers

I think everyone has seen this but here goes anyway.

http://www.powerstrut.com/psjan2005/fibergl182.jpg

Remember this is for solid unistrut and not slotted.  

Most of the time we see PS200 Uused (oftentimes slotted which makes it worse) and given the literature it can't much be used for anything other than branch lines and very short spans.

 

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources