Welded Built-up Slender Compressive WF Beam per AISC 2005 E7
Dear friends.
I have checked some beam that needed for the truss structure.
The structure needs the height of the beam 450mm.
Since the truss wide enough, the beam is laying down, means the the minor axis is perpendicular to gravity axis.
I've read the AISC LRFD 1999 and AISC LRFD 2005. I think the LRFD 2005 is missing the equation AISC-LRFD 1999 Specification Appendix B5.3d. (A-B5-15) ] that compute Flexural buckling stress based on K L and lamda_c.
This equation gave more lower stress buckling capabitity of the slender compressive member.Other equation on slender moved in AISC 2005 including Torsional and flexural-torsional buckling stress.
I need your opinion..
This the example:
UNIT SYSTEM : kN, m
SECTION PROPERTIES : Designation = H.450.320.8.16 in mm
Shape = I - Section. (Built-up)
Depth = 0.450,
Top F Width = 0.320,
Bot.F Width = 0.320,
Web Thick = 0.008,
Top F Thick = 0.016,
Bot.F Thick = 0.016,
Area = 1.35840e-002,
Asy = 6.82667e-003,
Asz = 3.60000e-003,
Ybar = 1.60000e-001,
Zbar = 2.25000e-001,
Qyb = 1.60720e-001,
Qzb = 1.28000e-002,
Syy = 2.36044e-003,
Szz = 5.46245e-004,
Zyy = 2.57153e-003,
Zzz = 8.25888e-004
Iyy = 5.31100e-004,
Izz = 8.73992e-005,
Iyz = 0.00000e+000,
ry = 1.97731e-001,
rz = 8.02121e-002,
rp = 0.00000e+000
J = 9.47883e-007,
Cwp = 4.11470e-006
DESIGN PARAMETERS FOR STRENGTH EVALUATION :
Ly = 5.01646e+000,
Lz = 5.01646e+000,
Lu = 5.01646e+000,
Ky = 1.00000e+000,
Kz = 1.00000e+000
MATERIAL PROPERTIES :
Fy = 3.65000e+005, Es = 2.00000e+008,
MATERIAL NAME = JIS SMA490W
Factored force/moments caused by unit load case.
Load combination ID = 34-
Pu = 2793.46 kN.
Muy = -7.27 kN-m.
Muz = -15.73 kN-m.
Vuy = 3.52 kN.
Vuz = -7.74 kN.
Check slenderness ratio of axial compression member (Kl/r).
SAME AS SUCCESSOR AISC 2005 E7
[ AISC-LRFD2K Specification B7. ]
Kl/r = 62.5 < 200.0 ---> O.K.
Check width-thickness ratio of flange (BTR).
[ AISC-LRFD2K Specification B5.1 ]
kc = 4/SQRT[h/tw] = 0.553 (for Built-up I-Section)
Lambda_r = 0.64*SQRT[Es/(Fy/kc)] = 11.14
BTR = bf/2tf =10.00 < Lambda_r-> NON-COMPACT SECTION !
Check depth-thickness ratio of web (DTR).
Lambda_r = 1.49*SQRT[Es/Fy] = 34.88
Dweb = H-tf1-tf2 = 0.42 m.
DTR= Dweb/tw = 52.25 > Lambda_r ---> SLENDER SECTION !
Compute elastic compressive stress.
NOT VERY DETAIL on AISC 2005, suggesting Fy for not repetition
Resistance factor for compression : phi = 0.85
f_lim = phi * Fcr = 295173.6487 KPa.
f_cal = Pu/Area - Muy*Ccom/Iyy = 208721.5030 KPa.
f = f_cal (if f_cal < f_lim)
Calculate effective depth of stiffened web (Bew).
[ AISC-LRFD2K Specification Appendix B5.3b (A-B5-12) ]
Be1 = (1.49*tw)/SQRT[Es/f] = 0.369 m.
1.91*tw [ 0.34 ]
Be2 = ---------- * [ 1 - ---------------- ] = 0.378 m.
SQRT[f/Es] [ (DTR)*SQRT[f/Es] ]
Bew = MAX(Be1,Be2) = 0.378 m.
Calculate reduction factor of stiffened elements (Qa).
[ AISC-LRFD2K Specification Appendix B5.3c. (A-B5-14) ]
A_eff = Area - (Dweb-Bew)*tw = 0.013 m^2.
Qa = A_eff/Area = 0.976
Full reduction factor for slender section (QsQa).
[ AISC-LRFD2K Specification Appendix B5.3d. (A-B5-17) ]
Q = Qs*Qa = 0.976
Calculate column slendness parameter (Lambda_c).
[ AISC-LRFD2K Specification E2. (E2-4) ]
(Kl/r) Fy
Lambda_c = -------- * SQRT[----] = 0.850
pi Es
Calculate critical stress (Fcr1, Fcr2).
Flexural buckling stress (Fcr1)
THIS EQUATION NOT MOVED AND GONE ON AISC 2005 E7
[ AISC-LRFD2K Specification Appendix B5.3d. (A-B5-15) ] ]
Lambda_c*SQRT[Q] = 0.840 < 1.5
Odr = Q*Lambda_c^2 = 0.706
Fcr1 = Q*(0.658^Odr)*Fy = 265167.1822 KPa.
Torsional and flexural-torsional buckling stress (Fcr2)
[ AISC-LRFD2K Specification Appendix E3 (A-E3-5) ]
Doubly symmetric shape
Gs = Es/(2(1+Poisson Ratio)) = 7.6923e+007 KPa.
Kx = 1.00 (Conservatively taken value).
L = 5.016 m.
Fe= [Pi^2*E*Cwp/(Kx*L)^2 + Gs*J]/(Iyy+Izz)=639725.8674 KPa.
Lambda_e = SQRT[Fy/Fe] = 0.755
Lambda_e*SQRT[Q] = 0.746 < 1.5
Odr = Q*Lambda_e^2 = 0.557
Fcr2 = Q*(0.658^Odr)*Fy = 282236.8864 KPa.
Calculate axial compressive strength (phiPn).
[ AISC-LRFD2K Specification E2. (E2-1), Appendix E3. (A-E3-1) ]
Fcr = MIN[ Fcr1,Fcr2 ] = 265167.1822 KPa.
phiPn = phi*Area*Fcr = 3061.73 kN.
Check ratio of axial strength (Pu/phiPn).
Pu 2793.46
------- = --------------- = 0.912 < 1.000 ---> O.K.
phiPn 3061.73
This the example:
UNIT SYSTEM : kN, m
Depth = 0.450,
Web Thick = 0.008,
Asy = 6.82667e-003,
Asz = 3.60000e-003,
Qyb = 1.60720e-001,
Qzb = 1.28000e-002,
Syy = 2.36044e-003,
Szz = 5.46245e-004,
Zyy = 2.57153e-003,
Zzz = 8.25888e-004
Iyy = 5.31100e-004,
Izz = 8.73992e-005,
Iyz = 0.00000e+000,
ry = 1.97731e-001,
rz = 8.02121e-002,
rp = 0.00000e+000
J = 9.47883e-007,
Cwp = 4.11470e-006
Ly = 5.01646e+000,
Lz = 5.01646e+000,
Lu = 5.01646e+000,
Ky = 1.00000e+000,
Kz = 1.00000e+000
Pu = 2793.46 kN.
Muy = -7.27 kN-m.
Muz = -15.73 kN-m.
Vuy = 3.52 kN.
Vuz = -7.74 kN.
1.91*tw [ 0.34 ]
Q = Qs*Qa = 0.976
(Kl/r) Fy
pi Es
L = 5.016 m.
Pu 2793.46
phiPn 3061.73