Pallet Bolier in bigger capacities
I am working on a project in Churchill Manitoba
My builidng heating load is about 600,000 btu/hr
and we wants to specify Pallet boiler the biggest boiler i could find is 100,000 btu/hr residential application
is any body had a chance using pallet boilers bigger than 100,000 btu/hr
we thinking may be two 300,000 btu/hr capacity commercial boiler manufactured in north america
Any body know any manufacturer who makes bigger boielr
thanks
RE: Pallet Bolier in bigger capacities
You are speaking of a relatively small boiler.  Since you seem to be looking for a heating boiler, I suggest you contact a reliable local HVAC boiler representative with your specific requirements.  There are many boiler manufacturers that should be able to easily fit your application.  600000 P/H is about 18 boiler horsepower.  With losses and running below rating (usually size to about 80% of rating), my guess is you need a 30 horsepower low-pressure (15 PSIG or lower), package boiler set up for HVAC.  Columbia and Cleaver Brooks might be a good start, but there should be many low pressure boiler manufacturers.
Need application data for more guidance.
Try www.crone.nl or ATS they have supplied pellet boilers up to 20.000.000 BTU in Canada.
I am looking for Pallet Boiler not the steam boiler