(OP)
What's the advantage of using auxiliary transformers ZNyn11 over Dyn11 (750KVA 11x.4KV)

Thanks

RE: Primary ZIg Zag

vreijb,
Z-winding is specified if neutral is not available for system grounding. This could be with auxiliary Y- winding or without. The zero sequence reactance of Z-winding is important for system grounding.
Hope it is helpful.  

RE: Primary ZIg Zag

several reasons go with Zig Zag primary:
a) need a grounded neutral on primary
b) need phase angle shift
c) apply reduced the primary insulation on primary
d) apply OLTC on primary at a lower vs on delta

RE: Primary ZIg Zag

(OP)
We have separate Z Transformer for neutral earthing. The client is asking ZNyn11 Transformer to reduce the gorund fault on low voltage side  

RE: Primary ZIg Zag

vreijb,
I must say it is a bad application to use zigzag primary just to reduce the ground fault current magnitude in 400V system. This can more simply done by adding a low ohmic resistor in the 400V neutral-to-ground circuit.
It is true that the Zigzag winding on primary will mean the zero sequence reactance for faults in 400V system would be of the order of 50%, reducing the ground fault current magnitude to just about 50% of the transformer rated current.

RE: Primary ZIg Zag

Hi,
Im second with Raghun.
It seems a very strange, use this type of trafo for reduce the ground fault sad.
More, I never see this type of trafo ZnYn11, once, for the distribution was used D(Y)zn... trafo.
Best Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources