What's the advantage of using auxiliary transformers ZNyn11 over Dyn11 (750KVA 11x.4KV)
Thanks
Thanks
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Primary ZIg Zag
Z-winding is specified if neutral is not available for system grounding. This could be with auxiliary Y- winding or without. The zero sequence reactance of Z-winding is important for system grounding.
Hope it is helpful.
RE: Primary ZIg Zag
a) need a grounded neutral on primary
b) need phase angle shift
c) apply reduced the primary insulation on primary
d) apply OLTC on primary at a lower vs on delta
RE: Primary ZIg Zag
RE: Primary ZIg Zag
I must say it is a bad application to use zigzag primary just to reduce the ground fault current magnitude in 400V system. This can more simply done by adding a low ohmic resistor in the 400V neutral-to-ground circuit.
It is true that the Zigzag winding on primary will mean the zero sequence reactance for faults in 400V system would be of the order of 50%, reducing the ground fault current magnitude to just about 50% of the transformer rated current.
RE: Primary ZIg Zag
Im second with Raghun.
It seems a very strange, use this type of trafo for reduce the ground fault
More, I never see this type of trafo ZnYn11, once, for the distribution was used D(Y)zn... trafo.
Best Regards.
Slava