Use of Solenoid Valve in Heat Pump Liquid Line

Use of Solenoid Valve in Heat Pump Liquid Line

Use of Solenoid Valve in Heat Pump Liquid Line

(OP)
Carrier Residential Heat Pumps specify that if lines are longer than 90ft that a bidirectional solenoid valve be placed in the liquid line near the outdoor unit to eliminate refrigerant being able to flow back into the Compressor unit during the OFF cycle.  

1) I am thinking that this must be to prevent the refrigerant from flowing back into the outside coil during HEATING mode?  Is this correct?  Is this a problem during COOLING mode?

2) is this a cure for a potential compressor "slugging" problem or is it to prevent the liquid from carrying heat from the building back outside and thus an efficiency issue?

2) Since these units use an "orifice" during heat pump HEATING mode, (instead of an expansion valve), the liquid can obviously flow back into the coil.  I am wondering if putting a HP expansion valve (one way expansion valve, other way just a check valve, same as used in the inside unit), in the heat pump outdoor unit liquid line, would work as well?  It seems like a hard cut off expansion valve would also prevent liquid flow back into the outdoor unit.

Can someone illuminate me on these points please?

Thanks.
Joe

RE: Use of Solenoid Valve in Heat Pump Liquid Line

The "drop" solenoid prevents refrigerant migration during the off cycle.  I believe the manufacturer is concerned with the total amount of refrigerant in the system once you get into longer pipe runs.  Liquid refrigerant will migrate to the coldest part of the system, then flood back to the compressor upon startup...and thats bad.  A mechanical expansion valve is not a positive "shut off" and will meter refrigerant whether the compressor is on or off.   

RE: Use of Solenoid Valve in Heat Pump Liquid Line

(OP)
Thanks for the information.  I was thinking that modern expansion valves DID provide a positive shutoff for refrigerant when the compressor was not running.  I notice that in both my heat pump and air conditioner, I can see liquid in the sight glasses when the compressors are stopped.  Since the pressure on the liquid side (when I measured it) was considerably higher than on the vapor side,  when the compressors were stopped, I had assumed that this meant the valves were operating as positive shut offs.  

However, I am not aware of exactly how much refrigerant an expansion valve will allow past after the compressor shuts off.  Obviously, the solenoid valve shuts off completely once the compressor shuts off.

The Infinity Heat Pump uses a metering orifice going into the outside coil during heating mode.  Does anyone know if the efficiency would be improved enough to matter if an expansion valve was used instead?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources